Is there anyone who want to exchange their knowledge about the protocol BSB / LPB Siemens ?
Currently I am able to read the parameters of the HVAC-controller, but I'm not able to change the values. I am willing to make available all that I have achieved.
amelia
|
|
|
Logged
|
|
|
|
ameliaamelia
Newbie
Offline
Posts: 16
Thank You
-Given: 252
-Receive: 2
|
|
« Reply #1 on: July 09, 2014, 12:24:52 12:24 » |
|
Step1 THE SIGNAL
CABLE two wires: 1- signal at 12+ volt; 2- signal GND.
FORMAT like the UART-TTL but with higher level of voltage; 12 volt = 1 0 volt = 0 4800 BAUDS [1 Start bit - 8 data bits - 1 ODD parity bit - 1 stop bit] (see HvacWriteMsgSignal.png).
VOLTAGE In Rx it is necessary to step down the voltage at the level of micro used 5.0 or 3.3 volt. In TX a step up.
INTERFACE The same cable is used by various devices, at my home they are 4, so the need to control the collisions. The schema is derived from the original done by <Daniel Heule>; I added same components to meet the following needs (see HvacInterfaceSCH.png): 1 LPB_LINE direct RX TTL level, used by the CMSA/CA collision detection function 2 TX_CTRL disable the output connection; 3 RX CTRL disable the input connection, so the micro UART-INTERRUPT is not fired; 4 GND 5 VCC 6 TX direct software formatted OUT signal, not sent through the UART-TX; 7 RX IN signal to UART-RX;
amelia
|
|
|
Logged
|
|
|
|
pablo2048
Active Member
Offline
Posts: 113
Thank You
-Given: 136
-Receive: 86
|
|
« Reply #2 on: July 09, 2014, 01:03:21 13:03 » |
|
|
|
|
Logged
|
|
|
|
ameliaamelia
Newbie
Offline
Posts: 16
Thank You
-Given: 252
-Receive: 2
|
|
« Reply #3 on: July 09, 2014, 07:48:59 19:48 » |
|
to pablo2048
I already googled for the subject and I also got your links. No one has complete information like message format, contents and so on. Today I solved my "write" problem and and will continue to publishing all my steps. Anyway, thank you.
amelia
|
|
|
Logged
|
|
|
|
Some Anon Guy
Junior Member
Offline
Posts: 43
Thank You
-Given: 58
-Receive: 25
|
|
« Reply #4 on: July 10, 2014, 02:23:09 14:23 » |
|
|
|
|
Logged
|
|
|
|
ameliaamelia
Newbie
Offline
Posts: 16
Thank You
-Given: 252
-Receive: 2
|
|
« Reply #5 on: July 10, 2014, 03:58:16 15:58 » |
|
to Some Anom Guy
I am using a Poscope logic analyzer as you con see at the image HvacWriteMsgSignal.png. The voltages involved are +12.0 to 5.0 or 3.3 (depending on microprocessor used). As stated before, now I am able to read-from and to set-to (change) the Siemens controller. As soon as possible I will continue to publish my work. Bye.
amelia
|
|
|
Logged
|
|
|
|
ameliaamelia
Newbie
Offline
Posts: 16
Thank You
-Given: 252
-Receive: 2
|
|
« Reply #6 on: July 12, 2014, 07:18:28 07:18 » |
|
Step2 THE MESSAGE
STRUCTURE byte 1 SYNC always 0xdc 2 DEVICE from with bit 7 (0x80) ON 3 DEVICE to 4 length of all the message from SYNC to last CRC 5 TYPE of message 6 COMMAND 1 7 2 8 3 9 4 10 DATA of variable length VL .. 10+VL byte 1 of 16 bit CRC-CCITT (XModem) 10+VL+1 2
DEVICE 0 RV61.843/160 - Siemens Controller (installed at my home) (1) 4 USER1 - My Application 1 5 USER2 - My Application 2 6 QAA75.611 - Room Control (1) 10 AVS37.294 - HVAC Front panel (1) 127 Broadcast (1)
(1) predefined TYPE 1 ? 2 Info 3 Set 4 ACK to Set 5 ? 6 Request 7 Reply to Request
COMMAND It is a 4 byte sequence; I coded it as it appears on the TYPE 4-ACK and 7-Reply. The messages TYPE 3-Set and 6-Request have the COMMAND-1 and COMMAND-2 inverted; the sequence is (in hex):
TX ...3d0507b0... RX ...053d07b0...
DATA The first byte has the value of 0x00 or 0x01; not sure, but I think that 0x00 = ENABLE and 0x01=DISABLE, it needs further investigation. The second byte and the following are the value. Every command has it FORMAT. I decoded all the command available on my QAA75-611, but I am still verifying the correctness. I found these:
FORMAT 10 C° bytes 2..3 / 64 11 C° ambient 1..2 (!) / 64 sent by QAA75-611 20 Seconds 2 30 Minutes 2..3 31 Minutes short 2 40 Hours 2..5 / 3600 41 Hours short 2 50 Days 2 80 Number 2..5 81 Number short 2..3 100 YY MM DD hh mm ss 2..9 101 hh:mm 2..3 (2) 102 DD:MM 2..3 (2) 103 YYYY 2..3 (2) 120 Options table 2 it is a single byte with various meanings, like a menu option
(2) to be verified
The code number of the FORMAT was assigned by me.
Attached is a part of my db, regarding the DHW section.
amelia
|
|
« Last Edit: July 12, 2014, 07:27:27 07:27 by ameliaamelia »
|
Logged
|
|
|
|
ameliaamelia
Newbie
Offline
Posts: 16
Thank You
-Given: 252
-Receive: 2
|
|
« Reply #7 on: July 13, 2014, 08:08:44 08:08 » |
|
Step2a THE MESSAGE UPDATE a
...
DATA The first byte: normally it has the value of 0x00; few commands can be set DISABLED or SET, the value in RX is 0x00 = SET and 0x01 = DISABLED or in TX 0x06 = SET and 0x05 = DISABLED.
...
amelia
|
|
|
Logged
|
|
|
|
ameliaamelia
Newbie
Offline
Posts: 16
Thank You
-Given: 252
-Receive: 2
|
|
« Reply #8 on: August 17, 2014, 02:01:46 14:01 » |
|
Step3 DIRECT WRITE TO HVAC
SUMMARY a - The communication BSB/LPB uses only one wire plus ground. b - Many users can read and write simultaneously. c - To avoid collision, the CMSA/CA protocol must be used. d - The bits must be inverted.
MICRO APPLICATION Language: C Micro: Microchip PIC32 32MX360F512L Frequency: 80 MHz
The TX uses the attached direct write to HVAC. The RX uses the standard USART port.
Actually I can read and write from/to the HVAC.
amelia
Attachment: the direct write function.
|
|
|
Logged
|
|
|
|
|